close
    Can a QO load center be used on the grounded "B" phase delta 240v,3ph-3w system?

    0  Views: 913 Answers: 1 Posted: 15 years ago
    Tags: electrical

    1 Answer

    Yes,the single phase convertilbe main lug only centers can be used on the Grounded "B"phase,240v,delta system.A&C phases will be connected to the bus bars.The B phase is connected to the neutral. Only QO-H2pole breakers can be used.


    Top contributors in Uncategorized category

     
    ROMOS
    Answers: 18061 / Questions: 154
    Karma: 1102K
     
    Colleen
    Answers: 47269 / Questions: 115
    Karma: 953K
     
    country bumpkin
    Answers: 11322 / Questions: 160
    Karma: 838K
     
    Benthere
    Answers: 2392 / Questions: 30
    Karma: 760K
    > Top contributors chart

    Unanswered Questions

    betrepublicpolska
    Answers: 0 Views: 2 Rating: 0
    qh88law
    Answers: 0 Views: 8 Rating: 0
    qh88law
    Answers: 0 Views: 7 Rating: 0
    Vinfast Kỷ Nguyên Xanh
    Answers: 0 Views: 6 Rating: 0
    hoangphatblog10vn
    Answers: 0 Views: 8 Rating: 0
    ex880com
    Answers: 0 Views: 9 Rating: 0
    tranquocanswceo
    Answers: 0 Views: 11 Rating: 0
    Sunwin
    Answers: 0 Views: 14 Rating: 0
    > More questions...
    563773
    questions
    779531
    answers
    926834
    users