close
    Can a QO load center be used on the grounded "B" phase delta 240v,3ph-3w system?

    0  Views: 856 Answers: 1 Posted: 14 years ago
    Tags: electrical

    1 Answer

    Yes,the single phase convertilbe main lug only centers can be used on the Grounded "B"phase,240v,delta system.A&C phases will be connected to the bus bars.The B phase is connected to the neutral. Only QO-H2pole breakers can be used.


    Top contributors in Uncategorized category

     
    ROMOS
    Answers: 18061 / Questions: 154
    Karma: 1102K
     
    Colleen
    Answers: 47269 / Questions: 115
    Karma: 953K
     
    country bumpkin
    Answers: 11322 / Questions: 160
    Karma: 838K
     
    Benthere
    Answers: 2392 / Questions: 30
    Karma: 760K
    > Top contributors chart

    Unanswered Questions

    35tjogocom
    Answers: 0 Views: 7 Rating: 0
    Hadiah bulananmu sudah siap menanti!
    Answers: 0 Views: 9 Rating: 0
    35tjogocom
    Answers: 0 Views: 7 Rating: 0
    35tjogocom
    Answers: 0 Views: 9 Rating: 0
    35tjogocom
    Answers: 0 Views: 7 Rating: 0
    35tjogocom
    Answers: 0 Views: 9 Rating: 0
    35tjogocom
    Answers: 0 Views: 10 Rating: 0
    kim882com
    Answers: 0 Views: 8 Rating: 0
    > More questions...
    517122
    questions
    752636
    answers
    861019
    users